Replies: 3 comments 1 reply
-
Yes, tf you use the Enhance Exercise add on there is a warm up parameter. If you are doing this via the buttons on the maintenance page you can push the start button, let it warm up, then the click the start and transfer button. If you are are doing the test by cutting the mains power, the timing of the engine starting after the power is loss and how long it will warm up is controlled by the controller firmware. Many of the residential generac units have a Start Up delay and a Warm Up delay parameter that can be set via the controller (liquid cooled Evolution models can set this from the web UI in genmon). |
Beta Was this translation helpful? Give feedback.
-
Was worried hitting start & transfer while it was running was a bad idea. Thank you for the clarification. |
Beta Was this translation helpful? Give feedback.
-
Just did the manual start , let the gen run a few minutes then tried to click the start and transfer tab but it does not transfer load. If it running when manually started the start and transfer button is disabled. |
Beta Was this translation helpful? Give feedback.
Uh oh!
There was an error while loading. Please reload this page.
-
I do a monthly manual start & transfer to let my gen run , warm up the oil and look at its output.
I notice it starts and transfers pretty quickly.
Does the transfer time have an adjustment parameter to delay transfer for 30 seconds , 45 seconds , etc. ?
Beta Was this translation helpful? Give feedback.
All reactions