Strong influence of air humidity on the heat flux #14752
Replies: 3 comments 2 replies
-
The default PATH_LENGTH for RADIATION is 10 cm. Using this over long distances over estimates the radiative absorption of atmospheric CO2 and WATER VAPOR.
|
Beta Was this translation helpful? Give feedback.
-
You can always get the post-fire conditions with post processing. If you know the PRODUCTS mass fraction and the H2O from fire only mass fraction, then you can add back in the humidty as it will be in constant ratio to the PRODUCTS based on the AIR defintion with the HUMIDITY present. A short path length will overestimate attenuation outside the flame at longer distances. The reverse is also true, that a long path length will underestimate at shorter distances. Atmospheric attenuation at 50 % humidty at 10 m is around 10 % and at 100 m is around 25 % (see Fig 66.36 in 5th SFPE Handbook). If you were to set the path length to the longest distance, your error at the smaller distances may not be that significant in comparison to the overall predictive uncertainties of FDS. The path length impacts the absorption coefficients globally. |
Beta Was this translation helpful? Give feedback.
-
Thanks for the detailed explanations! |
Beta Was this translation helpful? Give feedback.
Uh oh!
There was an error while loading. Please reload this page.
-
Good afternoon, colleagues!
We have two almost identical projects. There is a large object on fire, and a vertical platform 10 m away. We are interested in the value of the heat flux on this platform. We considered two situations when the humidity was 0% and 40%.
humidity_0.txt
humidity_40.txt
In the first case, the air composition was as follows
&SPEC ID='AIR' BACKGROUND=.True. SPEC_ID(1:3)='OXYGEN','NITROGEN','CARBON DIOXIDE' VOLUME_FRACTION(1:3)=0.208638049437029, 0.79096861006154, 0.000393340501431118/
In the second case
&SPEC ID='AIR' BACKGROUND=.True. SPEC_ID(1:4)='OXYGEN','NITROGEN','WATER VAPOR','CARBON DIOXIDE' VOLUME_FRACTION(1:4)=0.206659977922372, 0.783469534601562, 0.0094808761872295, 0.000389611288837626/
It turned out that the heat flux in our model is extremely dependent on the air humidity. Two fluxes differ by almost three times. (The total heat release in both situations was the same.)
I don't know what the effect of air humidity is on radiation absorption in real fires. Is it really that big? Maybe something in our model is configured incorrectly?
Beta Was this translation helpful? Give feedback.
All reactions