Strange results of devices #14657
mst-parkhachev
started this conversation in
General
Replies: 1 comment 3 replies
-
See 21.1 in the User's Guide This is due to velocity penetration error with the default FFT pressure solver on the zero-thickness OBST. You could: Make the walls one cell thick. This greatly reduces this error for the FFT solver. |
Beta Was this translation helpful? Give feedback.
3 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Uh oh!
There was an error while loading. Please reload this page.
-
Dear colleagues,
Let's give an example of a simplified project. Here we have a two-story building, and a small fire outside. The wall material is inert.
test.txt
The volume inside the building is not connected to the outside. However, DEVCs inside the building register strange values. This is especially noticeable on the top floor.
Why does this happen? In particular, where does the extra gas in the building come from? Why does temperature drop when pressure increases? Why is heat flux negative?
Beta Was this translation helpful? Give feedback.