Hello everyone,
I’m working on a using FDS and PyroSim, and I’ve encountered an issue where the peak Heat Release Rate in my model does not reach the value I expected based on the input data.
I’ve carefully set up the fire scenario and ensured that the input for the peak HRR is correctly defined, but the simulation results show a much lower peak HRR than anticipated.
I’ve double-checked the following:
I first set up the burner surface ramp up time to t^2 at 800s, and in the first run it only reached to about 75 MW. After that I set up the custom ramp up table to reach a fraction of 1/1 at 800s, and the results were almost an exact match to the first run, reaching only about 75 MW.
Despite the ramp up selection, the peak HRR seems to act similarly each time. My first thought is that FDS might have a max growth curve coefficient that is being capped out at. I thought that by defining the peak time/ growth curve you could manually create the growth curve coefficient.
Another thought is that I am simulating a heavy goods vehicle fire in a small tunnel, so the enclosure the fire takes place in is relatively small. If not enough oxygen can reach the fire, could this also be why the fire growth is stalling less than inputted? The reaction is an SFPE Polyurethane_GM37 fire. The tunnel has a grade of 3.95 which makes me think oxygen would be sufficiently supplied from downstream.
Has anyone experienced a similar issue or can offer insight into potential reasons why this might be happening? Thank you in advance!
Beta Was this translation helpful? Give feedback.