started this conversation in
General
Replies: 1 comment 1 reply
-
"Byte" in OPC UA is an unsigned byte. Try using the |
Beta Was this translation helpful? Give feedback.
1 reply
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Uh oh!
There was an error while loading. Please reload this page.
Uh oh!
There was an error while loading. Please reload this page.
-
Hello!
I try to write some variables to PLC use Milo 0.6.14, but not all variables are written.
In example below I write 4 variable: boolean control, byte index, byte output, int weight.
In PLC, these variables have the type: BOOL, BYTE, BYTE, DINT
boolean and int variable are being written successfully, but byte variables aren't.
I try changed type of variable in java to short, int, but it didn't help.
In PCL BYTE (0...255), in java byte (-128...127).
What am I doing wrong?
How do I write byte variables?
I'll notice, the reading byte variables was successful.
Please help me.
Thanks!
Beta Was this translation helpful? Give feedback.